as you can notice parts of Smart Home Forum by FIBARO is not available for you. You have to register in order to view all content and post in our community. Don't worry! Registration is a simple free process that requires minimal information for you to sign up. Become a part of of Smart Home Forum by FIBARO by creating an account.

 

As a member you can:

  •     Start new topics and reply to others
  •     Follow topics and users to get email updates
  •     Get your own profile page and make new friends
  •     Send personal messages
  •     ... and learn a lot about our system!

 

Regards,

Smart Home Forum by FIBARO Team


  • 0

Dimmer 2 overcurrent problem


treboR

Question

Hello,

 

I'm having a strange problem with multiple dimmer 2 modules.

 

When ever I connect a laptop charger ( of vacuum cleaner ) the modules will shut off and report overcurrent. After 5 seconds the light turns on again.

 

one of them has one Osram 30 - 105w transformer connected with 2 35w halogen spots behind it. So the load isn't the issue. The electric system is brand new ( new home ) and the modules are connected with 3 wires.

 

I've tried using a dimmer 2 bypass to maybe filter the "overcurrent" but that also does not work. This is pretty annoying since I have 40 of these in the house now. Would be a shame if this is normal..

 

Thanks in advance,

 

Robert

Link to comment
Share on other sites

Recommended Posts

  • 0
  • Inquirer
  • Oh lol sorry, I mean in a power socket that is connected to the same fuse.

     

    Sorry I was typing and watching TV at the same time

    Please login or register to see this image.

    /emoticons/default_smile.png" alt=":)" srcset="https://forum.fibaro.com/uploads/emoticons/[email protected] 2x" width="20" height="20" />

    Link to comment
    Share on other sites

    • 0

    just to get things straight

    the dimmer is at another socket then the vacuumcleaner?

    and the dimmer reports over current?

    if so, is the dimmer installed as it should?

    Link to comment
    Share on other sites

    • 0

    I'm pretty sure I've heard this before... But I don't know where... @treboR did you ask this question before, or perhaps on another forum?

    Anyway, some months ago, I connected a vacuum cleaner, a drill and a compressor unit (2-phase induction motor, 2.5 HP). I could make the lamp blink an instant, with the compressor. But I am reasonably sure that was due to the high inrush current of the motor. The dimmer does not shut down and does not report an alarm.

    You don't see any pattern to this? Like, some sockets influence some dimmers, but not others?

    Link to comment
    Share on other sites

    • 0
  • Inquirer
  • As far as I know I did not post this before because I did not have this problem with dimmer one.

     

    To make things more clear :

     

    The dimmer is connected to lights and nothing else. When turned on there is no problem ( unless some light flickering from time to time ? ) but as soon as I connect a laptop charger or vacuum cleaner ( on the same fuse as the dimmer creating a power surge, but should be no problem ) the dimmer shuts down and reports overcurrent.

    Link to comment
    Share on other sites

    • 0

    I understand. Overcurrent seems odd to me. Would be more logical to sense over voltage or under voltage, put also unlikely. The only thing that comes to mind... maybe you have bypass 1 connected. I know that can cause overcurrent.

    Link to comment
    Share on other sites

    • 0
  • Inquirer
  • No It's clearly a bypass 2.. But with or without it gives the same problem.

    Link to comment
    Share on other sites

    • 0

    I see. I hate to ask... but to eliminate another possibility... they're connected 100% as in the manual? Switches connected to Sx? And Sx not used for anything else? All "N" and "L" connections are really the same "N" and "L" per dimmer circuit? At the moment, I'm out of ideas. BTW what did support say?

    Link to comment
    Share on other sites

    • 0

    I have the same issue. When I start my vacuum cleaner (Miele with soft start) the light behind the dimmer 2, FGD212, goes down and comes back again after a few seconds. New home, 2-wire connection, correct connections, same fuse (and obviously the same phase). The dimmer is connected to lights and nothing else. Happens at several locations (different dimmers). My theory is that the vacuum cleaner creates s voltage drop that is sensed by the dimmer.

    Not really a problem, but not really the way it should be.

    Link to comment
    Share on other sites

    • 0

    I am no electrical expert here. Just sharing an observation which can be reproduced easily.

     

    Background:

    Circuit A which connects back to a MCB is a pure lighting circuit (national standard where lighting circuit is 6A and cannot mix with power socket) with a few sub-circuits for 2 or 3 9W LED lights each circuit and a dedicated sub-circuit for dimmable dining light. A Fibaro Dimmer 2 is connected only to this dimmable dining light, nothing else.

     

    Situation:

    Whenever other sub-circuits' lights are quick toggled on and off repeatedly for multiple times (e.g. 3 or 5 or 10 times, random pattern), it will cause errors (e.g. over current error) on Fibaro Dimmer 2 and switch off the dimmable dining light (consumes only 10W usually and up to 18W at max).

     

    I do not have the required electrical knowledge to analyse what may cause this. But this is reproducible and it cannot be the electrical circuits cause doing the same does not cause the same outcome with those other sub-circuits (which uses Fibaro 1x3kW Relay Switches).

    Link to comment
    Share on other sites

    • 0

    @treboR,

     

    You may want to try disable the 'auto-calibration' or any supposedly 'smart/intelligent' feature of this Dimmer 2. See if that helps.

     

    Just a suggestion based on a theory I have been thinking of.

    Link to comment
    Share on other sites

    • 0
  • Inquirer
  • @Chaicka,

     

    I'll give it a shot. Although the calibration process is only triggered at first power on. I've played with all kinds of settings ( burned out bulb detection, max load and even the percentage of current change ) and nothing changes.

     

    I have not contacted support about this.. But I wanted to know if I'm the only one ( thank god I'm not ). And like I say'd, my house is renovated but completely stripped. And the electric stuff is done by a company that wired everything with 3 wires.

     

    @petergebruers,

     

    The only thing that is different is that I use a normal phase wire on my momentary switches to pulse S1/S2. This should not be an issue since the switches are always open when not being manually used

    Link to comment
    Share on other sites

    • 0

    @Chaicka,

     

    I'll give it a shot. Although the calibration process is only triggered at first power on. I've played with all kinds of settings ( burned out bulb detection, max load and even the percentage of current change ) and nothing changes.

     

    I have not contacted support about this.. But I wanted to know if I'm the only one ( thank god I'm not ). And like I say'd, my house is renovated but completely stripped. And the electric stuff is done by a company that wired everything with 3 wires.

     

    @petergebruers,

     

    The only thing that is different is that I use a normal phase wire on my momentary switches to pulse S1/S2. This should not be an issue since the switches are always open when not being manually used

     

    The situation I face does not happen on day-to-day use. It only happens when other lightings-only sub-circuits within the same circuit is toggled on and off very very quickly for multiple times. The steps do not happen every day so it is not bothering much. 

    Link to comment
    Share on other sites

    • 0

    Connecting a switch to L instead of Sx is not recommended but I agree with you that reporting "over-current" does not seem to have anything to do with this...

    If FGD-212 reports "over-current" then it's almost certainly true. You cannot disable it. The detection protects the switching element and it is a fixed part of the dimmer. There is no parameter to influence it. I don't know if the dimmer could "accidentally" report an over-current... but I doubt it. It's one of the more important differences between the new and the old dimmer.

    Maybe the capacitive load of the LED can cause this if there is a sudden voltage change. I need to test that hypothesis.

    Maybe it also depends on the make/model of the LED.

    What kind of LEDs are you using? Would it be possible to try a different brand? I was testing with a Philips "Warm Glow" 9W (and it didn't show any problem).

    I'll try some other lamps & setups by the end of the week.

    Link to comment
    Share on other sites

    • 0
  • Inquirer
  • I'm not using led.. I'm using halogen spots behind the dimmer ( with an Osram transformer ). The reason I tried the bypass was because my supplier asked me to try it, but too bad it did not make any difference.

     

    I can get you some more info about these parts if you want. I can reproduce the error here any time I want

    Please login or register to see this image.

    /emoticons/default_smile.png" alt=":)" srcset="https://forum.fibaro.com/uploads/emoticons/[email protected] 2x" width="20" height="20" />

    Link to comment
    Share on other sites

    • 0

    The bypass keeps the voltage on the LED low when the dimmer is nearly off and that solves issues with LED and CFL that glow or flicker when the dimmer is turned off. You reported issues with the dimmer "on", when the bypass is "off". So knowing the operating principle, it doesn't surprise me that it did not have a positive effect. If you ever decide go with LED lighting, it's possible you need one of those. It depends...

    When you say "Osram transformer" you mean a "Halotronic"? Do you know the part number?

    I can't think of eny experiment at the moment. I'll try to find a combination of load & trigger (transformer, adapter) that has the same effect.

    Link to comment
    Share on other sites

    • 0
  • Inquirer
  • With the Osram transformers I mean these guys

     

    Please login or register to see this link.

     

    This is the exact same type.

    Link to comment
    Share on other sites

    • 0

    Connecting a switch to L instead of Sx is not recommended but I agree with you that reporting "over-current" does not seem to have anything to do with this...

    If FGD-212 reports "over-current" then it's almost certainly true. You cannot disable it. The detection protects the switching element and it is a fixed part of the dimmer. There is no parameter to influence it. I don't know if the dimmer could "accidentally" report an over-current... but I doubt it. It's one of the more important differences between the new and the old dimmer.

    Maybe the capacitive load of the LED can cause this if there is a sudden voltage change. I need to test that hypothesis.

    Maybe it also depends on the make/model of the LED.

    What kind of LEDs are you using? Would it be possible to try a different brand? I was testing with a Philips "Warm Glow" 9W (and it didn't show any problem).

    I'll try some other lamps & setups by the end of the week.

     

    The phenomena I shared have been observed by my supplier across several consumers' installation and no specific brand or model of LED lights. And it happens only if other switching within same circuit (links back to same 6/10A MCB) and the switching is done very very fast pace (on off on off on off on off on off - faction of seconds per toggling).

     

    I am using Philips LED 9W down lights. I can take a video clip to show how to reproduce it.

    Link to comment
    Share on other sites

    • 0

    Thanks for the extra information. I know enough to make a test setup.

    Link to comment
    Share on other sites

    • 0

    Hello Peter,

     

    I have the exact same problem. In my bedroom I have a dimmer2, all wires (3 wire system) connected correctly (100% sure). It's a new house and new electricity wires.

     

    The light is working well, I can dim up and down, switch on and off. But as soon as I put a vacuum cleaner, a drilling machine (anything with high power) in one of the other wall outlets in my bedroom, the light turns off and the home center reports an overcurrent message.

     

    However, the funny thing is that my bedroom and livingroom are on the same fuse. If I put on a vacuum cleaner in my living room, then the light in the bedroom just stays on the way it should be.

     

    It looks like the more close you get to the location of the dimmer, the higher the chance it reports an overcurrent. It's weird behaviour and for sure not the way it should be.

    Link to comment
    Share on other sites

    Join the conversation

    You can post now and register later. If you have an account, sign in now to post with your account.

    Guest
    Answer this question...

    ×   Pasted as rich text.   Paste as plain text instead

      Only 75 emoji are allowed.

    ×   Your link has been automatically embedded.   Display as a link instead

    ×   Your previous content has been restored.   Clear editor

    ×   You cannot paste images directly. Upload or insert images from URL.

    ×
    ×
    • Create New...