as you can notice parts of Smart Home Forum by FIBARO is not available for you. You have to register in order to view all content and post in our community. Don't worry! Registration is a simple free process that requires minimal information for you to sign up. Become a part of of Smart Home Forum by FIBARO by creating an account.

 

As a member you can:

  •     Start new topics and reply to others
  •     Follow topics and users to get email updates
  •     Get your own profile page and make new friends
  •     Send personal messages
  •     ... and learn a lot about our system!

 

Regards,

Smart Home Forum by FIBARO Team


  • 0

Wire FGS-223 in parallel with another switch?


MikeG

Question

Hi, I hope you are all well.

 

I would like to replace a couple of X10 modules with an FGS-223. The only potential problem is that one of the lights has another switched feed coming into it (as per the attached addition in red). This is something that I inherited and can't change and I also don't have the option to wire this feed into the S1 or S2 inputs of the module due to the situation of the light and this other cable. It's all on the same phase/circuit.

 

Irrespective of whether this is a "good idea" or not, it has worked reliably with the X10 switches (or as reliable as X10 ever is!) for over 10 years.

 

Would switching 240VAC to Q1 or Q2 (when the module outputs are set to "off") damage the FGS-223?

 

Regards,

Mike

Please login or register to see this attachment.

Link to comment
Share on other sites

2 answers to this question

Recommended Posts

  • 1

Will be fine, I have a similar setup with a 240v pir so the sensor or fibaro module can both control the load. Potential will be the same on q1 whichever is turned on.

As long as you are absolutely sure they are the same phase and rcd all will be ok 8-)

Link to comment
Share on other sites

  • 0
  • Inquirer
  • 12 hours ago, Abacus said:

    Will be fine, I have a similar setup with a 240v pir so the sensor or fibaro module can both control the load. Potential will be the same on q1 whichever is turned on.

    As long as you are absolutely sure they are the same phase and rcd all will be ok 8-)

     

    Brilliant - thanks for taking the time to reply. :)

     

    Link to comment
    Share on other sites

    Join the conversation

    You can post now and register later. If you have an account, sign in now to post with your account.

    Guest
    Answer this question...

    ×   Pasted as rich text.   Paste as plain text instead

      Only 75 emoji are allowed.

    ×   Your link has been automatically embedded.   Display as a link instead

    ×   Your previous content has been restored.   Clear editor

    ×   You cannot paste images directly. Upload or insert images from URL.

    ×
    ×
    • Create New...