as you can notice parts of Smart Home Forum by FIBARO is not available for you. You have to register in order to view all content and post in our community. Don't worry! Registration is a simple free process that requires minimal information for you to sign up. Become a part of of Smart Home Forum by FIBARO by creating an account.

 

As a member you can:

  •     Start new topics and reply to others
  •     Follow topics and users to get email updates
  •     Get your own profile page and make new friends
  •     Send personal messages
  •     ... and learn a lot about our system!

 

Regards,

Smart Home Forum by FIBARO Team


  • 0

Smart implant to control fan based on DS18B20


k1s21

Question

Hello I've been trying to get a fan running triggered by temperatures measured by DS18B20 probes.

 

The Fan is 12V and according to the spec needs max 0.08A, so I tried first a 12V 1A PSU to power both, but by the time i was wired up it had only 10.5 V at the fan connection.  I tried another PSU, this time 12V 1.5A but only 10.8V at the fan connection - not sufficient to make the fan spin.

 

If the maximum current on the outputs is 150mA, why is the fan's 80mA / 0.96W not being received through the Smart Implant ?

 

The wiring from the PSU to the Smart Implant is 2cm.  From the implant to the fan is 1 metre (using the cable supplied with the PSU ~12-14 AWG I thnk)

 

 

 

Please login or register to see this attachment.

 

Edited by k1s21
Link to comment
Share on other sites

14 answers to this question

Recommended Posts

  • 0

@k1s21

I ask, do you have a DC motor? It can be an AC motor. Are you sure it's DC?
Is it some type of PC fan? Send the exact type.
Is the fan only two-wire? Doesn't need a PWM folder?
Some fans also come with a thermistor that actively controls the speed-based temperature(it inserts its own resistance into the circuit).
it's weird that doesn't get move with such a small drop voltage. In practice, different voltage dividers are made to slow down the fan speed and these then turn more slowly even at 5V.
Do you have a Stabilized 12V DC power supply?
I suggest the following procedure:
Connect the fan to the power supply only - is it spinning? If so, disconnect the DS18 sensors from the SI and connect the SI to the power supply - is the fan rotating?

Edited by Martin_N
Edit: i wrote some bad words
Link to comment
Share on other sites

  • 0
  • Inquirer
  • Hello Martin,

    Thanks for your reply 

    Yes the fan (Noctua NF-A20 PWM) works fine when plugged in directly to a 12V 1A supply (or 12V 1.5A) - I don't know if they're "Stabilized" - they came with IP cameras

     

    As a PWM fan it has 4 wires but only the two for +ve and -ve are connected (I haven't got any of the supplied "Low Noise" adapters connected.  The 2x DS18B20 and smart implant are all powered from the same PSU

     

    Disconnecting the DS18B20s would mean de-soldering (some tidy work ;) ) .  Do you think the tiny electrical demand of the probes is causing that voltage drop?

    Edited by k1s21
    Link to comment
    Share on other sites

    • 0

    @k1s21

    I assume you tried to measure with an ohmmeter that the SI outputs are switching. Isn't there a mistake in my own performances? Check this first.
    It could happen that a short circuit on the circuit passed through the output. (for example by connecting a wire on a fan). Then the fan survived, but the SI output remained as a fuse ... :(

    The power supplies to the cameras are stabilized, so the drop in voltage will be a mystery. In addition, at a given current, a fairly large cross-section (small AWG) of wire to the fan and a short distance should be practically no accommodation.
    I assume that you have used a black wire for - and yellow wires for + on the fan.
    If so, disconnect the fan from the SI and connect only the wires that switch the SI output.
    Is it spinning? ... No = look for a problem in the power supply or fan.
    Yes = return the wires to SI, but the interchange is between them (I think there are no relays, but optocouplers and something doesn't work like me).

    Link to comment
    Share on other sites

    • 0

    I think you are overloading the smart implant. The fan will have an inrush current of many times the steady state current of 0.08A. When the fan it not spinning it will try to draw this high current and you may damage the smart implant.  The way to get around this is to have the smart implant drive a slave relay, and the relay then drives the fan.

     

    Post back if this solves your issue!

    Link to comment
    Share on other sites

    • 0

    Unless your Smart Implant is defective, running your fan should work.
    Have you measured how much current your fan draws when you run it directly against the voltage adapter?

    How do you trigg the output?

     

    I tested this with a three speed fan on a UBS that has the same performance as the Smart Implant and the fan was able to run at all three speeds.

    (UBS with mini relay CPC1008N)


    Low speed 72 mA (starting current 94 mA)
    Medium speed 112 mA (starting current 150 mA)
    High speed 148 mA (starting current 200 mA)

     

    Edited by RH_Dreambox
    Link to comment
    Share on other sites

    • 0
  • Inquirer
  • Well,

     

    I've discovered that the fan never draws more than 0.15A 

    Yes, the Smart Implant outputs are switching.

    It seems Output 1 delivers 12V but Output 2 only 10V.

     

     

    Link to comment
    Share on other sites

    • 0

    @k1s21

    Really interesting information. Did you measure the voltage empty or with the fan connected?
    It really looks like a damaged output. Be that as it may, I believe that the fan should run slower even at 10V.
    When you state that the current does not exceed 0.15A, I understand that it is close to value. So it depends on what measuring instrument you use. If you don't have True RMS, you don't have to catch a peak that exceeds just 0.15A.

    If you know that the SI is really damaged, try to disassemble it and take a picture of it from the inside. Unfortunately, I do not have any and I would be interested in the internal construction. According to some models, it should be different from the Universal Binary Sensor.

     

    Link to comment
    Share on other sites

    • 0
  • Inquirer
  • I measured it empty with the -ve electrode on the output screws and the +ve at the power input.

     

    The current draw I see is simply looking at the multimeter screen as I switch power on until after a second or so it settles down to 0.08A. 

     

    I'm not inclined to open it if is defective, in case I can return it under warranty. Unfortunately not much help from Fibaro support.  Simply a short message: "Output 1 and output2 don't deliver any voltage. It's a dry-contact/ Potential free"

    Link to comment
    Share on other sites

    • 0

     

    I found a picture of SI. Although it looks more like a model than a photo, I can already make a picture.

    From what I can see, this is not "dry contact" in the true sense of the word - it's more of a relay contact term.
    I understand that the output may appear this way, the optocouplers and SSR relays are similar and always switch some minimal voltage.
    There are really used optocouplers that galvanically separate the circuits. There will still be protective diodes for the outputs on the underside of the SI.
    I've never thought about it, but depending on the internal connection, it may depend on how you connect the entire circuit.
    If you now switch +, try changing the connection and switching -.
    I'm guessing the diode was damaged.

     

    Please login or register to see this spoiler.

     

    Link to comment
    Share on other sites

    • 0
    On 12/4/2021 at 8:54 AM, Tim__ said:

    I think you are overloading the smart implant. The fan will have an inrush current of many times the steady state current of 0.08A. When the fan it not spinning it will try to draw this high current and you may damage the smart implant.  The way to get around this is to have the smart implant drive a slave relay, and the relay then drives the fan.

     

    Post back if this solves your issue!

    Hi Tim, I believe your suggestion would also solve my issue. I'm trying to drive a water pump, but as soon as the pump activates, the volts drop rapidly until the pump stops. So far no damage to pump or implant. I have a relay but I'm wondering if you're able to give some advice about the wiring as I'm pretty confused and can't see to find much information/diagrams, except for suggestions like yourself to use one. Appreciate any advice!

    Link to comment
    Share on other sites

    • 0

    Hi @aots74 - nice to see another Aussie here :-)

     

    Here's a pic I stole off the web.  Replace the "starter switch" with the Smart Impant two terminals called "OUT1" (you can control a second pump using "OUT2"). You can buy a suitable relay from Jaycar - just make sure that the coil voltage matches your solenoid voltage (usually 12V or 24V, could be AC or DC.  Preferably DC as this is what the impant uses); and that the contacts are rated for the pump inrush current. Provide + and - power to the Implant (other connections not needed).  

    ELECTRICAL SOLENOID STARTER SLAVE RELAY ISUZU GENUINEimage.png.ba22308d89a49a71fb3fb354bd24cddf.png

    Link to comment
    Share on other sites

    • 0

    Thanks @Tim__! I ended up figuring it out and it was a bit of a mess, but once I had it hooked up it made sense. Basically, the implant (on both side), relay (on both sides) and pump all connected to - , the implant and relay both connected to +, then the control line of out 1 connected to the in line on the relay. Dunno if that really made sense but when I get a chance I'll do up a diagram! Thanks again for your help :)

    Link to comment
    Share on other sites

    • 0

    Glad you got it working, and thanks for reporting back!

    Link to comment
    Share on other sites

    Join the conversation

    You can post now and register later. If you have an account, sign in now to post with your account.

    Guest
    Answer this question...

    ×   Pasted as rich text.   Paste as plain text instead

      Only 75 emoji are allowed.

    ×   Your link has been automatically embedded.   Display as a link instead

    ×   Your previous content has been restored.   Clear editor

    ×   You cannot paste images directly. Upload or insert images from URL.

    ×
    ×
    • Create New...