as you can notice parts of Smart Home Forum by FIBARO is not available for you. You have to register in order to view all content and post in our community. Don't worry! Registration is a simple free process that requires minimal information for you to sign up. Become a part of of Smart Home Forum by FIBARO by creating an account.

 

As a member you can:

  •     Start new topics and reply to others
  •     Follow topics and users to get email updates
  •     Get your own profile page and make new friends
  •     Send personal messages
  •     ... and learn a lot about our system!

 

Regards,

Smart Home Forum by FIBARO Team


Recommended Posts

Posted

Hi,

i use a Fibaro FGRM 222 Roller shutter with fhem and a new electronic motor with obstacle detection.

The limit switches are set and the blinds can be operated with normal switches.

 

 

With the FGRM 222 i have a problem.

The calibration was successful.
 

When switching the relay is closed and the LED lights up.

Then the relay drops off again directly and the motor does not work.

After switching 4 to 5 times the motor moves.

 

With a mechanical motor, the actuator is functioning properly.

 

Can you change a parameter so that the motor works with the fibaro actuator?

 

Please excuse my bad english.

 

Posted

Electronic limit switches should do just fine, please adjust parameter 17 to longer time and monitor power consumption when blind is moving and after it stops, then adjust parameter 18 properly.

  • Topic Author
  • Posted

    Thanks for the help.

    I have Parameter 18 changed to value 0. Other values did not work.

    So Parameter 17 was not funktional any more. The contact turned off only after several minutes.

    So I changed Parameter 22. I have measured the operational time of the motor. This time I have adjusted on Parameter 22.

    Now it works. Is that ok?

    Posted

    So the motor was operating despite reaching limit switches?

  • Topic Author
  • Posted

    The actuator has opened the contact only after several minutes.

    The motor stopped reaching the limit switch.

    The contact was under voltage for a long time. With Parameter 22 the contact opens short time after reaching the limit switch now.

    Posted

    So the limit switch was not detected - parameter 18 was wrongly set. What are power values when blind is moving and after stop?

    • 3 weeks later...
  • Topic Author
  • Posted

    I don't know how i can see this

    The fhem-Reading shows in sup-item power 0.0W during blinds drive and also after stop.

    Join the conversation

    You can post now and register later. If you have an account, sign in now to post with your account.

    Guest
    Reply to this topic...

    ×   Pasted as rich text.   Paste as plain text instead

      Only 75 emoji are allowed.

    ×   Your link has been automatically embedded.   Display as a link instead

    ×   Your previous content has been restored.   Clear editor

    ×   You cannot paste images directly. Upload or insert images from URL.

    ×
    ×
    • Create New...