as you can notice parts of Smart Home Forum by FIBARO is not available for you. You have to register in order to view all content and post in our community. Don't worry! Registration is a simple free process that requires minimal information for you to sign up. Become a part of of Smart Home Forum by FIBARO by creating an account.

 

As a member you can:

  •     Start new topics and reply to others
  •     Follow topics and users to get email updates
  •     Get your own profile page and make new friends
  •     Send personal messages
  •     ... and learn a lot about our system!

 

Regards,

Smart Home Forum by FIBARO Team


FGD 212 Dimmer 2


Recommended Posts

Guest spazpeker
Posted

i have just fitted the dimmer 2 replacing an existing Fibaro dimmer

I have 23 6w megaman LED's total wattage 138 it worked fine with the old dimmer but with the dimmer 2 I have to ramp the brightness slowly or it switches off

Posted

I don't have this type of load, nor the amount of load, but I know Parameter 39, Overload can be raised from 250 to 350 Watt. Does that help? What is the result of Parameter 31 (dimming type)?

Guest spazpeker
  • Topic Author
  • Posted

    I don't have this type of load, nor the amount of load, but I know Parameter 39, Overload can be raised from 250 to 350 Watt. Does that help? What is the result of Parameter 31 (dimming type)?

    Yes Already upped it to 350 31 was detected as trailing edge
    Posted

    What type of installation do you have? 2- or 3-wire?

    What result do you have in parameter 30?

    Can you send me more data about your load? Exact model or there is sometimes rated current written on the bulb.

     

    Is there a possibility to log in to your system, and check what error it is sending?

    Posted

    I hope nobody gets offended if I join this topic, but I own the Dimmer 2 and I try to learn about it as much about as possible... To help other people. So I have a question, but if it's too much trouble then you really don't need to put any effort in this. The question is: how many of these lamps CAN be driven without any problems (roughly)? That would give me an idea of the amount of load (but with different lamp types) I would need to test with...

    Posted

    All loads have a startup current, as all the LED lights contain their own little power supply they also have a startup current (called an inrush current). Depending on the load this can be 10 - 15 higher than the average current, which in your case means somethings like 1300 Watt for a few ms. Therefor the dimmer may not like it when you turn them all on to a 100% and go into a protection mode.

    Please login or register to see this image.

    Guest spazpeker
  • Topic Author
  • Posted

    What type of installation do you have? 2- or 3-wire?

    What result do you have in parameter 30?

    Can you send me more data about your load? Exact model or there is sometimes rated current written on the bulb.

     

    Is there a possibility to log in to your system, and check what error it is sending?

    I have tried both currently it is left as a three wire for the last 18 months the room has been working fine with the old fibaro dimmer in 2 wire mode no bypass

    parameter 30 is control mode

    23 of MEGAMAN 6W 400LUMEN GU10 DAYLIGHT 

     

    it should be 138w when turned on slowly at full brightness the dimmer 2 says 141w

     

    no error is sent

    Guest spazpeker
  • Topic Author
  • Posted

    All loads have a startup current, as all the LED lights contain their own little power supply they also have a startup current (called an inrush current). Depending on the load this can be 10 - 15 higher than the average current, which in your case means somethings like 1300 Watt for a few ms. Therefor the dimmer may not like it when you turn them all on to a 100% and go into a protection mode.

    Please login or register to see this image.

    it wont even go to 50% worked fine with the normal dimmer

    Posted

    even then the power supply will turn on and create a high current peak. 10 times (50% of 138) 69 is still 690 Watt that will try to go through the dimmer for a short time. Most dimmers can handle an inrush current but a dimmer that handles only 250Watt might have a problem with this, and don't forget that the first dimmer was 500Watt.

     

    Try to take out a few bulbs and it will probably have no problems... (Just as a test)

    Posted

    Can anyone tell me when the Dimmer 2 will be available in Australia?

    Guest fat
  • Topic Author
  • Posted

    Can anyone tell me when the Dimmer 2 will be available in Australia?

    +1 for that. Hopefully soon otherwise I might have to use Qubino modules which will be available in September here in Australia

    Guest fat
  • Topic Author
  • Posted

    Any ETA Fibaro for this in Australia? We are still waiting for the wall plug and smoke sensor as well

    Posted

    Any solution for this problem with the non working load, it seems I have the same problem.

    My load is 3x25W.

    Posted

    3x25W standard lights or are those LED lights? With LED you could probably use the FIbaro by-pass 2. If it is a normal light it should work, if it doesn't the dimmer does not meet the specifications and therefor faulty.

    Posted

    Those are standard lights, if I turn them on with the physical button they turn on with no fuzz but if I try to turn them on by a scene or in the HC than they turn on for a second and then off again. I had the old dimmer before and just changed to the new one. Any idea?

    Posted

    do you have more scenes that control the dimmer? looks like something just turns it off again... Can you show your scene?

    Posted

    I have deleted the dimmer once again and it is now not even assigned to a room or a device so it shouldn't be affected by any scene. I will try to change the dimmer and see that it is not damaged in any way. Could it be that the lights are coming to its end?

    Posted

    BTW: Is the bypass 2 part of the dimmer 2 product or must i buy it separately?

    Posted

    It is sold separately.

    Posted

    I have deleted the dimmer once again and it is now not even assigned to a room or a device so it shouldn't be affected by any scene. I will try to change the dimmer and see that it is not damaged in any way. Could it be that the lights are coming to its end?

     

    Magnus, in the manual there is a tip that may help You. If the light is connected in 2 wire mode, there is a possibility, that calibration algorithm sets to high dimming level.

    Try to change parameter 2. in this case manually to a lower value.

    Join the conversation

    You can post now and register later. If you have an account, sign in now to post with your account.

    Guest
    Reply to this topic...

    ×   Pasted as rich text.   Paste as plain text instead

      Only 75 emoji are allowed.

    ×   Your link has been automatically embedded.   Display as a link instead

    ×   Your previous content has been restored.   Clear editor

    ×   You cannot paste images directly. Upload or insert images from URL.

    ×
    ×
    • Create New...