as you can notice parts of Smart Home Forum by FIBARO is not available for you. You have to register in order to view all content and post in our community. Don't worry! Registration is a simple free process that requires minimal information for you to sign up. Become a part of of Smart Home Forum by FIBARO by creating an account.

 

As a member you can:

  •     Start new topics and reply to others
  •     Follow topics and users to get email updates
  •     Get your own profile page and make new friends
  •     Send personal messages
  •     ... and learn a lot about our system!

 

Regards,

Smart Home Forum by FIBARO Team


  • 0

Aeotec ZWA009 aërQ Temperature & Humidity Sensor


Question

Posted

Does this sensor works with HCL ? What about dew & mould ? Has anyone tested ?

10 answers to this question

Recommended Posts

  • 0
Posted (edited)

From product description, temp and humidit should be fine, dew point is same any other multilevel sensor, so these will work without template. The weather alarm (moisture) notification will probably not work, same probably for high/low temp notification. I was about to test it ... but wasn't able to buy it any, the european aeotec distributor - wave europe - does not have any of them, no even listed.

 

 

Edited by tinman
  • 0
Posted

I have two, but I do not have it in HCL but in HC3. Temperature, Humidity and Dew point are fine. I do not see Mould there. My guess is the same will be with HCL. It reports High moisture as binary sensor, but I cannot confirm if it works or not as I am not using it in my automation. I set notification scene with Humidity sensor as condition.

 

With Mould description on Aeotec site I think it is calculated. Unfortunately I did not find formula yet. If it is calculated, then you need Lua, which is officially not possible in HCL.

 

I have two of these sensors, but I have installed only one of them.. I'm waiting for S2 to launch so I can test it on this device.

  • Like 2
  • 0
Posted

According to Aeotec website, it has been tested and it is compatible:

Please login or register to see this link.

 

  • 0
Posted

  

On 12/29/2020 at 8:56 PM, tinman said:

From product description, temp and humidit should be fine, dew point is same any other multilevel sensor, so these will work without template. The weather alarm (moisture) notification will probably not work, same probably for high/low temp notification. I was about to test it ... but wasn't able to buy it any, the european aeotec distributor - wave europe - does not have any of them, no even listed.

 

 

 

I bought mine here:

Please login or register to see this link.


I arrived there trough a link at aoetec web and the just sells aetoec products, seems to be something like the aeotec store.  Whatever, they send it to Spain so assumed to the rest of europe too

 

On 12/30/2020 at 8:59 AM, jakub.jezek said:

I have two, but I do not have it in HCL but in HC3. Temperature, Humidity and Dew point are fine. I do not see Mould there. My guess is the same will be with HCL. It reports High moisture as binary sensor, but I cannot confirm if it works or not as I am not using it in my automation. I set notification scene with Humidity sensor as condition.

 

With Mould description on Aeotec site I think it is calculated. Unfortunately I did not find formula yet. If it is calculated, then you need Lua, which is officially not possible in HCL.

 

I have two of these sensors, but I have installed only one of them.. I'm waiting for S2 to launch so I can test it on this device.

 

 

This is how looks on HCL

 

Please login or register to see this image.

/monthly_2021_01/imagen.png.78cdac2f4100bc0d93c3469bc8b6b70b.png" />

 

1st Icon= No idea, 2nd Supposed to be Warning mold could appear (or somethig like that). The rest are obious.

  In case of being possible and you know how on   

Please login or register to see this link.

    we have a full set of parameter to adjust. I don' find out how and will be very grateful if someone one give a hand. 

  • 0
  • Inquirer
  • Posted (edited)
    On 1/24/2021 at 2:22 PM, baliya said:

    I don' find out how and will be very grateful if someone one give a hand. 

     

    Parameters are :

     

     

     

     

    index="1" instance="1" label="Minimum Temperature change to report" max="100" min="0" size="1" type="byte" value="20">

    This value defines the minimum change of temperature to cause an unsolicited report of humidity to the central controller using Lifeline.

      If the value is set to 0, there will be no reports sent to the controller, when the temperature changes.
      However, periodic reports, managed by configuration parameter 4, may still be active.
       
       index="2" instance="1" label="Minimum humidity change to report" max="20" min="0" size="1" type="byte" value="5">
      This value defines the minimum change of humidity to cause an unsolicited report of humidity to the central controller using Lifeline.
      If the value is set to 0, there will be no reports sent to the controller, when the humidity changes.
      However, periodic reports, managed by configuration parameter 4, may still be active.
       
      index="4" instance="1" label="Periodic Reports" max="65535" min="0" size="2" type="short" units="seconds" value="43200">
      This parameter defines the time interval to send an unsolicited report.
      If the value is set to 0, there will be no periodic reports sent to the controller.
      However, reports on temperature/humidity changes, managed by configuration parameters 1 and 2, may still be active.
       
       index="5" instance="1" label="Temperature Upper Watermark value" max="1000" min="0" size="2" type="short" units="1/10 degree" value="0">
      This parameter defines a temperature.
      If the measured temperature surpasses this watermark a BASIC command is sent into Association Group 2
       
       index="6" instance="1" label="Temperature Lower Watermark value" max="1000" min="0" size="2" type="short" units="1/10 degree" value="0">
      This parameter defines a temperature.
      If the measured temperature dropps below this watermark a BASIC command is sent into Association Group 3
       
       index="7" instance="1" label="Humidity Upper Watermark value" max="90" min="0" size="1" type="byte" units="%" value="0">
      This parameter defines a relative humidity.
      If the measured relative humidity surpasses this watermark a BASIC command is sent into Association Group 4
       
       index="8" instance="1" label="Humidity Lower Watermark value" max="90" min="0" size="1" type="byte" units="%" value="0">
      This parameter defines a relative humidity.
      If the measured temperature drops below this relative humidity a BASIC command is sent into Association Group 5
       
      index="9" instance="1" label="Low Temperature Trigger BASIC Set Command Value" max="255" min="0" size="1" type="byte" value="0">
      This defines what BASIC command shall be sent out into association group 3
       
       index="10" instance="1" label="High Temperature Trigger BASIC Set Command Value" max="255" min="0" size="1" type="byte" value="0">
      This defines what BASIC command shall be sent out into association group 2
       
      index="11" instance="1" label="Low Humidity Trigger BASIC Set Command Value" max="255" min="0" size="1" type="byte" value="0">
      This defines what BASIC command shall be sent out into association group 5
       
       index="12" instance="1" label="High Humidity Trigger BASIC Set Command Value" max="255" min="0" size="1" type="byte" value="0">
      This defines what BASIC command shall be sent out into association group 4
       
       index="13" instance="1" label="Offset value for Mould danger notification" max="10" min="0" size="1" type="byte" value="0">
      This value allows to increase the humidity threshold for mould danger notification by max 10%
       
       index="255" instance="1" label="Reset Parameter" max="14294967295" min="0" size="4" type="int" write_only="true" value="0">
      This parameter helps reset configuration parameters and the device to factory defaults

     

     

     

    All you need is this :

     

    Please login or register to see this attachment.

    Edited by BurnerMan
    • 0
    Posted
    2 hours ago, BurnerMan said:

     

    Parameters are :

     

     

     

     

    index="1" instance="1" label="Minimum Temperature change to report" max="100" min="0" size="1" type="byte" value="20">

    This value defines the minimum change of temperature to cause an unsolicited report of humidity to the central controller using Lifeline.

      If the value is set to 0, there will be no reports sent to the controller, when the temperature changes.
      However, periodic reports, managed by configuration parameter 4, may still be active.
       
       index="2" instance="1" label="Minimum humidity change to report" max="20" min="0" size="1" type="byte" value="5">
      This value defines the minimum change of humidity to cause an unsolicited report of humidity to the central controller using Lifeline.
      If the value is set to 0, there will be no reports sent to the controller, when the humidity changes.
      However, periodic reports, managed by configuration parameter 4, may still be active.
       
      index="4" instance="1" label="Periodic Reports" max="65535" min="0" size="2" type="short" units="seconds" value="43200">
      This parameter defines the time interval to send an unsolicited report.
      If the value is set to 0, there will be no periodic reports sent to the controller.
      However, reports on temperature/humidity changes, managed by configuration parameters 1 and 2, may still be active.
       
       index="5" instance="1" label="Temperature Upper Watermark value" max="1000" min="0" size="2" type="short" units="1/10 degree" value="0">
      This parameter defines a temperature.
      If the measured temperature surpasses this watermark a BASIC command is sent into Association Group 2
       
       index="6" instance="1" label="Temperature Lower Watermark value" max="1000" min="0" size="2" type="short" units="1/10 degree" value="0">
      This parameter defines a temperature.
      If the measured temperature dropps below this watermark a BASIC command is sent into Association Group 3
       
       index="7" instance="1" label="Humidity Upper Watermark value" max="90" min="0" size="1" type="byte" units="%" value="0">
      This parameter defines a relative humidity.
      If the measured relative humidity surpasses this watermark a BASIC command is sent into Association Group 4
       
       index="8" instance="1" label="Humidity Lower Watermark value" max="90" min="0" size="1" type="byte" units="%" value="0">
      This parameter defines a relative humidity.
      If the measured temperature drops below this relative humidity a BASIC command is sent into Association Group 5
       
      index="9" instance="1" label="Low Temperature Trigger BASIC Set Command Value" max="255" min="0" size="1" type="byte" value="0">
      This defines what BASIC command shall be sent out into association group 3
       
       index="10" instance="1" label="High Temperature Trigger BASIC Set Command Value" max="255" min="0" size="1" type="byte" value="0">
      This defines what BASIC command shall be sent out into association group 2
       
      index="11" instance="1" label="Low Humidity Trigger BASIC Set Command Value" max="255" min="0" size="1" type="byte" value="0">
      This defines what BASIC command shall be sent out into association group 5
       
       index="12" instance="1" label="High Humidity Trigger BASIC Set Command Value" max="255" min="0" size="1" type="byte" value="0">
      This defines what BASIC command shall be sent out into association group 4
       
       index="13" instance="1" label="Offset value for Mould danger notification" max="10" min="0" size="1" type="byte" value="0">
      This value allows to increase the humidity threshold for mould danger notification by max 10%
       
       index="255" instance="1" label="Reset Parameter" max="14294967295" min="0" size="4" type="int" write_only="true" value="0">
      This parameter helps reset configuration parameters and the device to factory defaults

     

     

     

    All you need is this :

     

    Please login or register to see this attachment.

     

    Thks for your response.

    Allready tried with no succed, and neither this time??  Wait a minute... yes it works, more or less. My error was no to read all the labels. Due a wrong translatios of the interface or whatever the value appears in the wrong place.

     

     

    Please login or register to see this image.

    /monthly_2021_01/imagen.png.2c64bd733ff1683f23aaf1c5e996d30d.png" />

     

    I've sent the template to fibaro, as aeotec is well knownand popular may be they will do something.... Let's hope so

    • 0
  • Inquirer
  • Posted (edited)

    I'm new here and while searching the forum around I found out that FIBARO doesn't care about their customers. They will never make the template. I hope to prove me wrong, but.......

    Edited by BurnerMan
    • Like 2
    • 0
    Posted

    So you were right :) 

    • 0
    Guest swissnet3000
    Posted

    Which value should be set for the temperature transfer. After how many seconds should the temperature value be sent? 3600 sec ?

     

    • 0
    Posted
    W dniu 15.08.2021 o 23:19, swissnet3000 napisał:

    Which value should be set for the temperature transfer. After how many seconds should the temperature value be sent? 3600 sec ?

     

    Were you able to change this parameter? Each time I'm changing to shorter time, after change and refresh time is changed, but when I'm login again this value is back to 3600 sec. I'm using HC3

    Join the conversation

    You can post now and register later. If you have an account, sign in now to post with your account.

    Guest