RS3 + Nice era inn actions s 620 (venetian blind)
KimHG
Hello
If you change slat from 10% to 20%, slat does not work. However, if you go from 10% to 90%, it will open but not 90%.
It seems that the motor needs some stating time when changing the slat angle.
However, none of the parameter values have anything to do with it.
There is only time from 0 to 100% of slat .
Is there no way to solve this?
Hi @KimHG,
I would check parameter 155 to set it to 70% - 80% of total motor consumption. Lets say in case of 100W motor set param 155 to 75 Watts. Then do calibration again and check slats control afterwards. Should be correct or significantly better.
Oh, and do not forget to set Role as Venetian blinds. Sometimes people forgot to set that. But since you wrote you can control slats, you probably did that.
  • Hello
    Calibration has been completed normally.
    There seems to be some delay time when the motor is running.
    There is no problem when opening and closing the blinds, but there is a problem when changing the tilt angle.
    If the tilt angle is changed at once as the blindden is opened or closed, it will be reflected as accurately as the tilt angle input.
    However, if  I change only the tilt angle, the angle value does not reflect properly. For example, when you change from 10% to 30%, the angle changes by 20% rather than 30%. If I change 10% to 20% here, the angle itself will not change. It seems that the motor does not immediately respond to the signal when it is initially driven.
    I think it has a soft start function in this motor, but I do not know how to apply it to the fibaro roller shutter.