HEM - power metering query
AutoFrank
I have a Home Energy monitor (HEM2) and have the clamp in the main live into my meter box to try and understand what the house is drawing power wise.
I seem to be getting two power readings that are different with both changing over time but none seem fully accurate. One power reading seems accurate some times and the other power reading seems more accurate at other times if I look at what is running in the house at the time.
I have only one clamp but the inclusion created 12 devices in in total
1471 (device id = 1471)
1471.0 & 1471.0.1, 1471.0.2 (device ID 1472, 1473, 1474)
1471.1 & 1471.1.1, 1471.1.2 (device ID 1475, 1476, 1477)
1471.2 & 1471.2.1, 1471.2.2 (device ID 1478, 1479, 1480)
1471.3 & 1471.3.1, 1471.3.2 (device ID 1481, 1482, 1483)
I can get power readings on 1472 & 1475
1472 - api details (power = 895.79w)
1475 - api details (power = 2.44 kw)
The energy readings from both are the same
/monthly_2016_12/HEM.PNG.047bc402ddb8466bdc8544922ce1ed7e.PNG" alt="HEM.PNG" />
Does anybody know which parameter I should be using
thanks
frank
Edited by AutoFrank
hi
did you manage to figure out which sensors are what?
i have just bought this but the 2 sensor version.
i managed to work out that the 1st and 2nd set seem to be for clamp 1
3rd set is clamp 2 and 4th set is clamp 3
but my voltage is always showing as 140v? instead of the expected 240v?
I have HEM with 1 clamp and it works perfectly. After monitoring group 1 and 2 for some time I selected group 2 since it is showing same readings as i have on my UPS. When installing HEM it is very important to connect supply wires correctly, brown to live (L) and blue to neutral (N) for 1 clamp version or 3 clamp version while 2 clamp version supply wires must be connected between phases (live) as it is show on the installation leaflet. Also clamps have markings on them K -> L and it is very important that they are installed properly with L facing circuit breaker for EU version that is.
So, @morpheus75,
You have 2 clamp EU version so check that you connected two supply cables properly, blue wires to live phase 2, first clamp brown to live phase 1 and second clamp to live phase 3. Then you also must install clamps on the same phase from which it has supply, first clamp on phase 1 and second clamp on phase 3.
BTW 2 clamp version can only be used on 3 phase supply system.
  • Hi @morpheus75
    I have a single clamp version and haven't been able to figure out if it is 1 or 2 as they both seem correct at given times
    I'll need to take extra readings to try and determine..
    _f
    i bought the 2 clamp version.
    1 to monitor my house usage and 2nd clamp to monitor my solar.
    there are 2 power leads. i have powered both from my house.
    so i should power the 2nd clamp from the solar supply?
    will give that a try tonight.
    cheers guys
    cheers guys
    According to the Aeotec instructions 2 clamp meter in EU can be used on 3 phase 3 wire systems only so I don't think that you can get it to work properly on 1 phase system with two different power sources. You should buy two 1 clamp HEM and then connect them to each system separately, one for main power to the house and one for your solar system. But of course, I could be wrong. What makes me think that I'm right is Aeotec instructions and that you have wrong measurement of the voltage.
    This is usually because voltage is different between phases and between phases and neutral for ∛ and your 2 clamp meter supply is supposed to be connected between phases which is  times 240V is around 400V. Your meter is showing 140V which is exactly for  less than 240V !!!
    Anyway please be careful with electricity and take necessary preparations before putting hands in the electrical box. Also make sure that HEM supplies blue wires are not connected inside HEM to same terminal because if they are, then connecting them to two different power supplies will make possibly unwanted bridge that can do damage to your equipment!
    @Sankotronic
    cheers for info and i think you are right. i did re-read instructions again and the numbers do add up.
    thanks for warning re electricity but i forgot to mention that im qualified electrician aswell.
    i thought i could get away with using 1 meter and 2 clamps but looks like gonna have to get 2 separate units........
    cheers
  • 14 hours ago, morpheus75 said:
    @Sankotronic
    cheers
    @morpheus75, Thanks., I'm going to use the same approach so I ordered a second HEM for my panels.
    @Jamie mccrostie
    Question for the electricians among you..
    This is the way my panels are setup. The electrician said the electricity from the panels is harmonised with the rest of the house
    I have one HEM in place at the moment and was thinking about putting the second on the AC supply from the panels (two red dots)
    will this work to give me how much the house if taking and what my panels are generating ?
    @Jamie mccrostie
    Hem 2 yes.
    Hem 1 yes but will it cope when your generating more power than your using and its being pumped back into supply grid, I think you can set it up so it doesn't operate if it senses current flow is in reverse, but Im guessing that.
    Thanks @Jamie mccrostie
    Ill have to see how it goes
    I suppose I could get a third HEM and install it in reverse.
    Actually now taht you mention it i'm seeing some full readings on the HEM I have installed (between channel 1 and 2) , I wonder if this is related to the reverse flow situation....
    I wonder how other people have solved this ?
    @AutoFrank
    HEM 2 should be connected between the inverter and the main utility box. the power from panels to inverter is DC and not AC and is of the 500v magnitude.
    HEM 1 hopefully will have a setting for reverse detection.
    (i am a solar electrician aswell)
    Just googled it and there is parameter to stop recording if reverse flow detected so as long as you can use that as a trigger you can compare with code
    Thanks @morpheus75
    In the drawing its in the AC side, I assume it doesn't matter if it is on one side of the trip v the other side as long as it's on the AC side ?
    @Jamie mccrostie
    So it sounds like I'll need a third one to get the info I want ?
    @AutoFrank
    I think Franks drawing shows it in the right spot
    1 minute ago, AutoFrank said:
    Thanks @morpheus75
    @AutoFrank
    from your diagram it shows that the PV is connected to the fuse inside your main board so you need to clamp to this supply to measure the power for the solar alone
    Basically connect the clamp between INVERTER and HOUSE MAINS
    Edited by morpheus75
    update
    1 minute ago, morpheus75 said:
    @AutoFrank
    Yes but the inverter is feeding a sub board first which may or my not have other out going circuits as well so thats where he needs his clamp for the solar measurement.
  • 39 minutes ago, morpheus75 said:
    @AutoFrank
    @morpheus75
    @Jamie mccrostie
    Perfect .. hopefully I'll have it in a few days and can try that
    .. but it does look like I'll need a third one to get the data I need :-(
    It actually will still be cheaper as a Smart meter from our electricity supplier is €350 (HEM's are €80) and it looks more like a dumb meter :-( than a smart meter as I don't think the home owner can query it at all.
    Thanks a lot guys ....
    Edited by AutoFrank
  • @Jamie mccrostie
    @morpheus75
    I may have found a parameter for reverse flow that may solve the reverse flow part
    from
    14 minutes ago, AutoFrank said:
    @Jamie mccrostie
    @morpheus75
    from
    Frank, maybe you do need three with the extra one reversed at mains switch in. It would only measures when solar generated power is feeding back into grid otherwise you cant see the house usage in this state.
    Then you could compare values between generated and (Mains supply in or Mains supply out) to find house usage.
    I think you're correct @Jamie mccrostie , now that I've read it again, The parameter looks like it may just report as positive a negative vale if the clamp is reversed and not positive for 'inflow' and negative for 'outflow'. I think I'll start another post in case somebody has done this before
  • Hi @Jamie mccrostie, @morpheus75, @jompa68, @Sankotronic, @petergebruers
    I've all three HEM installed in my effort to measure what my PV panels are generating and whether the house is drawing extra from the grid or sending excess back to the grid.
    One HEM on the PV Panel that is matching the readings on the cloud app I have :-)
    I have two HEM installed clamps (2 separate HEM devices) in the incoming cable into the house and am looking at the configuraton part now
    The two clamps are installed  with the direction on the clamp opposite to each other.
    The idea here is to measure power when the house draws from the grid and and when the house (PV panels is sending excess power to the grid)
    This is the reference in the data sheet to parameter 2
    It looks like I should configure my HEM measuring outbound current as negative only (value = 3) and the HEM measuring inbound power as positive only (value = 2)
    I am now wondering if I should have installed both clamps in the same direction instead of opposite to each other
    Lastly if I was at the parameter is it as simple as this ....
    _f